RE: [datacenter] Generators
> Also, don't buy too much generator. Buy an inductive ammeter and see what
> the your real load of your NOC is. Double that. One of my local
> competitors bought 10x more than they could ever use,.
One caveat... If you've got a UPS between the genset and the load, you
need to actually double the _maximum capacity of the UPS_ rather than
double the _actual load_. UPSes tend to dump the full load plus the
battery recharge load all at once, which is a lot of instantaneous
application of torque to the genset. Takes a bit of an oversize engine to
power through that without stalling.
-Bill
---------------------------------------------------------------------