Re: [datacenter] Seal the room for clean agent fire suppression



% > 	in my limited experience, sealing the room is worth the
% > 	effort/expense.  sealing a dropped ceiling is kind of like
% > 	sealing a raised floor.  Do it as asecondary containment
% > 	perimiter.
% 
% 
% I may be misunderstanding, but when I tested with ceiling tiles
% not sealed, the tiles just blew off and opened the space to the
% rest of the facility not allowing for any integrity. Hence, the
% discharge worked, but the effect of the discharge was minimized
% by inability to pressure.
% 
% As far as sealing rock vs. tile, I would think the leaks would
% be minimal and if you could measure the effects of pinhole leaks
% on gas discharge, I'd be interested in the ramifications.


	sounds more like a simple miscalulation on space/presure
	to me.  I'm not sure that there is a single answer here.
	Most places I've been in do a single perimeter, seal it,
	and presurize to that volume.  Some places do multiple
	perimeters, seal them, and presurize per volume.  Thats
	a tactic that requires a bit mroe disipline and may not 
	be worth the cost.

-- 
--bill